Hi People,
Last year I managed to control the CO2 in the room with the following configuration
But I must have made some changes that it is not working this year... :(
The idea is the CO2 socket will be ON for 5 minutes, stop, wait 2min30sec and turn on again if the conditions below prevail.
Light sensor must be above 65%, the Temp sensor below 29C and the CO2 sensor Below 1200ppm.
Why its not working, what am I missing?
Hope some guru of the forum will help me, please.
Regards,
Roberto
I don't like the CO2 Hyst of only 1ppm set this little more like 50ppm to not flip.
The mistake is you using a Impuls timer and bring the CO2 signal where usually goes Day/Night in ?
Make the Impuls timer correct with day night signal only and connect it with another and Function with the real dosing signal
Risposta
Prova a fornire una risposta sostanziale. Se fosse necessario commentare la domanda o la risposta, usa lo strumento per i commenti. Puoi sempre rivedere le risposte - non è necessario rispondere due volte alla stessa domanda. Inoltre non dimenticarti di votare - selezionare le migliori domande e risposte aiuta molto!