Welcome!
This community is for professionals and enthusiasts of our products and services.
Share and discuss the best content and new marketing ideas, build your professional profile and become a better marketer together.
CO2 Room programming
Version: 1.2
Theme: Functions Programming the SGC
на 31.07.23 г., 15:27 ч. • 2,046 разглеждания
Hi People,
Last year I managed to control the CO2 in the room with the following configuration
But I must have made some changes that it is not working this year... :(
The idea is the CO2 socket will be ON for 5 minutes, stop, wait 2min30sec and turn on again if the conditions below prevail.
Light sensor must be above 65%, the Temp sensor below 29C and the CO2 sensor Below 1200ppm.
Why its not working, what am I missing?
Hope some guru of the forum will help me, please.
Regards,
Roberto
I don't like the CO2 Hyst of only 1ppm set this little more like 50ppm to not flip.
The mistake is you using a Impuls timer and bring the CO2 signal where usually goes Day/Night in ?
Make the Impuls timer correct with day night signal only and connect it with another and Function with the real dosing signal
Вашият отговор
Моля, опитайте да дадете състоятелен отговор. Ако искате да коментирате въпроса или отговора, просто използвайте инструмента за коментиране. Моля, помнете, че винаги можете да ревизирате отговорите си - не е нужно да отговаряте на един и същ въпрос два пъти. Освен това, моля, не забравяйте да гласувате - това наистина помага да изберете най-добрите въпроси и отговори!
За тази общност
Themes
Инструменти за въпроси
Статистика
Зададен: 31.07.23 г., 15:27 ч. |
Видян: 2046 времена |
Последно актуализирано: 3.08.23 г., 6:37 ч. |